(02-09-2015, 08:23 AM)jonny round boy Wrote:(02-09-2015, 07:37 AM)kingfisher Wrote: Has as been said. Although not notifiable the circuit still has to be tested and paper work provided.
Ok, so exactly what tests are required? What paperwork must be provided, and to whom?
The tests are dependant on what work was done. A visual check that all services (gas, water, etc) are earthed and appropriate sized cable is used and correct protective devices is a start, usually followed by at least a Zs test and insulation test. The Zs is a good one as it also picks voltage and polarity as well.
There are generally 2 options for the "paperwork" either a "full blown" installation certificate or a "small works certificate". The paperwork is given (whilst retaining copies) to the person who ordered the work.